Check the gas pressure, You should have a static gas pressure (with no appliances on) of 14" of water colum. With all the stove burners on and the water heater burner on, you should have 11" of water colum. If the heater does not have 11" of w.c., it will not fire up. The gas pressure regulator on your propane tanks will have to be replaced. You didn't say how old your trailer is. The gas pressure regulator last about 7 to 12 years. Also you didn't say if you had ignition spark, (sounds like a clicken sound). It should go through 3 trys. Reset the thermostat on try again. If no ignition spark check the sail switch.(tales the furnace of correct air pressure) Check voltage at the furnace, if you have low voltage the furnace wouldn't work correctly.